It seems to me that I am allowed to reclassify the dimming wire, and run it with the power conductors.
I'm thinking the MC cable with the separated wired for dimming is for when someone can't reclassify the dimming wires, doesn't want to reclassify the dimming wiring, or for jurisdictions where codes or the AHJ doesn't allow this.
After all, all of my Class 2 wiring would be in conduit, and the terminations would still be enclosed with the power conductors at the light fixture and at the dimmer box.
Anyhow, for this particular project I wound up specifying wireless controls.
I'm thinking the MC cable with the separated wired for dimming is for when someone can't reclassify the dimming wires, doesn't want to reclassify the dimming wiring, or for jurisdictions where codes or the AHJ doesn't allow this.
After all, all of my Class 2 wiring would be in conduit, and the terminations would still be enclosed with the power conductors at the light fixture and at the dimmer box.
Anyhow, for this particular project I wound up specifying wireless controls.