I had a contractor recently disagree with my call on an underground installation. The contractor was installing PVC schd 80 as a raceway for power and communications to a sign. The first inspection out was for the power conduits (buried 30" down), no problem. A few days later I get a second underground inspection for this site. I go out and the contractor has installed PVC schd 80 about 8"-12" from grade. I question what it's for and he says they already had filled the trench to that point and realized they forgot a raceway. I call him on table 300.5 (min 18") and he says he does not have to meet 18" because it is only for communications, no line power. I refer him to table 300.5, where it says 0-600v. He disagrees, I issue a Notice of Violation, he goes to my boss.
Now, I know it is not an electricution issue, since it is comm cables, but I would think the owner of the property would be ticked if they accidentlly dug up this conduit.
What do you think? Was I wrong?
Now, I know it is not an electricution issue, since it is comm cables, but I would think the owner of the property would be ticked if they accidentlly dug up this conduit.
What do you think? Was I wrong?