What would happen in two completely isolated systems, say generators for simplicity, if one hot leg from one system makes direct contact with the hot leg from the other system. With no direct path back to source, would there be any current flow?
Can you elaborate on this?the first connection simply establishes the voltage relationships between the two systems.
Two wires connected to the same point will be equal in potential because they are electrically continuous. What that potential will be depends on where you call "ground" for the sake of measurement.In a single system, when you bond two things, their potential attempts to equalize. Whether that be for the purpose of equipotential bonding (pools) or when you have a normal circuit and load etc.
With two separate isolated systems, I can’t see the motivation for two points from each system to seek equipotential.
A voltage difference between two points occurs when there is something pushing charge between the two points (from one to the other in the case of DC, or back and forth in the case of AC). If you have point A connected to system 1 which is isolated from system 2 which contains point B, there is nothing pushing charge between A and B. uCan you elaborate on this?
A little thing I like to call "creative wiring".I saw a couple of low voltage systems where there were only 3 wires available and both AC and DC was needed. They tied one leg of both systems to a common conductor so they could get both AC and DC at the other end using only 3 conductors.
That first connection is often via a grounded conductor from each system. So unless both systems are identical voltage systems that are "in phase" with one another and it is the "same phase conductor" making contact, which is what they do when they intentionally parallel sources with each other, there is likely to be a voltage between the two conductors mentioned in OP. Amount of current that flows will depend on what that voltage is and how much impedance is in the circuit path. The closer to being in phase they are the lesser the voltage will be between them.Can you elaborate on this?
It would have to be completely isolated, so at most one system could be a grounded system (X0 connected to earth). If both systems are grounded, then that common connection to earth is already the first connection between the systems, so you will be able to measure voltage.If I go X1 on one system, then to X0 on another isolated system I would get 0 volts again yeah?
Right. Good clarification.It would have to be completely isolated, so at most one system could be a grounded system (X0 connected to earth). If both systems are grounded, then that common connection to earth is already the first connection between the systems, so you will be able to measure voltage.
Cheers, Wayne
In the real world you will often have some amount of coupling capacitance so a 'phantom' voltage might be noticed. This is the principle behind some non-contact voltmeters.....go X1 on one system, then to X0 on another isolated system I would get 0 volts again yeah?
So voltage is completely limited to what you’re measuring it to then. If I take one meter lead to a 120v main lug and the other to a cookie, I’ll read 0 volts because they have no continuity at all. If I go X1 on one system, then to X0 on another isolated system I would get 0 volts again yeah?