I was asked to present a short 15 minute presentation on Direct Line Starting a 3-phase electric motor.
I have compiled the following and would ask that for any additional input and/or corrections.
I am using a 7.5 HP motor @ 208 VAC
General Information:
Direct line starting is also referred to as across the line or full voltage starting. In this configuration the motor current is the same as the line current. The voltage at the motor terminations is as the same as the line voltage.
Disadvantages to this configuration: The stator requires high current draw during start up and may damage the windings of three phase induction motors. Devices along the line may also be affected by voltage drop during start-up of the motor.
Common Uses:
Water pumps, compressors, fans, and conveyor belts
Calculations:
A. Disconnecting Means @ motor feeder:
Type-430.109
Single motor 115% FLC
24.2 amps x 115% = 27.83 amps
30 amp disconnect
B. Branch circuit over current protection:
Note: Short circuit & ground fault protection with ability to carry motor starting current(Complies with 430.52 (b) and (c))
430.52
FLC x the following:
Non time delay fuse 300% min / 400% max
Time delay fuse 175% min / 225% max
Inst trip breaker 800% min / 1300% max
Inverse time breaker 250% min / 300% max
C. Branch Circuit Conductors:
430.22
125% of motor FLC
430.150
7.5 HP @ 208 V 3 ph = 24.2 amps
24.2 x 125%=30.25
310.16
30.25 = 10 AWG @ 35 amps (75 degree C)
Apply temperature/deration factors as required)
D. Motor Controller
430.83
Types: HP rated Switch, Inverse Type CB, General Use Switch for 300 V or less/2 HP or less
7 1/2 HP motor = 7 1/2 HP rated controller
E. Overload Protection
430.32 (A)(1)
No service factor given
No temp rise given
All other motors 115%
No nameplate rated current available, use FLC from 430.250
24.2 x 115%=27.83 amps
F. Motor Ful Load Current
430.250
7.5 HP @ 208 V 3 ph = 24.2 amps
Thanks for taking the time to add any input, I appreciate it!
I have compiled the following and would ask that for any additional input and/or corrections.
I am using a 7.5 HP motor @ 208 VAC
General Information:
Direct line starting is also referred to as across the line or full voltage starting. In this configuration the motor current is the same as the line current. The voltage at the motor terminations is as the same as the line voltage.
Disadvantages to this configuration: The stator requires high current draw during start up and may damage the windings of three phase induction motors. Devices along the line may also be affected by voltage drop during start-up of the motor.
Common Uses:
Water pumps, compressors, fans, and conveyor belts
Calculations:
A. Disconnecting Means @ motor feeder:
Type-430.109
Single motor 115% FLC
24.2 amps x 115% = 27.83 amps
30 amp disconnect
B. Branch circuit over current protection:
Note: Short circuit & ground fault protection with ability to carry motor starting current(Complies with 430.52 (b) and (c))
430.52
FLC x the following:
Non time delay fuse 300% min / 400% max
Time delay fuse 175% min / 225% max
Inst trip breaker 800% min / 1300% max
Inverse time breaker 250% min / 300% max
C. Branch Circuit Conductors:
430.22
125% of motor FLC
430.150
7.5 HP @ 208 V 3 ph = 24.2 amps
24.2 x 125%=30.25
310.16
30.25 = 10 AWG @ 35 amps (75 degree C)
Apply temperature/deration factors as required)
D. Motor Controller
430.83
Types: HP rated Switch, Inverse Type CB, General Use Switch for 300 V or less/2 HP or less
7 1/2 HP motor = 7 1/2 HP rated controller
E. Overload Protection
430.32 (A)(1)
No service factor given
No temp rise given
All other motors 115%
No nameplate rated current available, use FLC from 430.250
24.2 x 115%=27.83 amps
F. Motor Ful Load Current
430.250
7.5 HP @ 208 V 3 ph = 24.2 amps
Thanks for taking the time to add any input, I appreciate it!