disco for detached garage

Status
Not open for further replies.
Re: disco for detached garage

Guys , Even though I disagree that 6 breakers in a panel would be code compliant , even if it was code compliant your panel would have to be suitable for use as service equipment.Art 225.36


Donnie
 
Re: disco for detached garage

Donnie do you agree that six throws of the hand are allowed for the service disconnect of a buildings service from the POCO?

I see this a lot to save money on 480 volt GFP breakers.

Come from a pad mount transformer to switch gear with no main but 3, 4, 5 or 6 breakers each rated less than 1000 amps.

Now when you turn all these breakers off the switch gear is still hot unless the POCO pulls the cut outs.
 
Re: disco for detached garage

Donnie, I don't think anyone would argue that 225.36 would apply.

Now, as Bob says 225.33 is the key.

225.33 references 225.30 which is a prerequisite for 225.31, which is a prerequisite for 225.32, which is a prerequisite for and brings us back to 225.33.

Roger
 