Question, a homeowner has a gazebo with a subpanel. The spa is 10 feet away from the sub panel. Could I use the sub panel and put a 60 GFI breaker as a disconnect for the spa?
 

Federico

Member
Location
Arizona
Occupation
Electrician
Sorry the spa is 50a The feeders coming from the main panel is #4 wire 80a that feeds the sub panel the gazebo has lights fan and outlets small fridge
 

Federico

Member
Location
Arizona
Occupation
Electrician
It has the neutral ground separate in the sub panel not tied in together. I’m just trying to avoid trenching pass the spa to a wall and then come back to the spa. It will be a lot easier just to put a breaker GFI 50 amp in the sub and just go 6ft. of pipe and 4ft. of seal tight to the spa
Buy code does it needs a separate disconnect? I just can’t used the sub panel?
 