disco

Status
Not open for further replies.

normbac

Senior Member
Is there a general rule on requirement to install a disco or not
for instance if an ac condensor is two foot from a panel, can panel be used as disco (non fuse requirement)
208 3 phase 30a water heater is 12 feet from visible panel, is disco required?
I am not clear on why some things require and others do not any easy way to know without reading codes in detail TIA
 
iwire said:
A disconnecting means must be within sight and no more then 50' away.
So a breaker is considered a means of disco i get it, but what is the rule of thumb for what requires a disco
 
Norm, your question really is "May the OCPD be the disconnect, or is a separate disco required?"

The answer is that the OCPD may be the disco, as long as it meets the requirements of the disco.
 
celtic said:
Have you checked 440.12(D) ['05]

IMHO, these are not "rules of thumb".
it is not ac units in general I am talking about 240 volt & up compressors, water heaters, ac condensors etc is there a reason for some requiring a disco and some not? sorry for the confusion TIA
 
LarryFine said:
Norm, your question really is "May the OCPD be the disconnect, or is a separate disco required?"

The answer is that the OCPD may be the disco, as long as it meets the requirements of the disco.
Yes that was part of my question Thanks
 
normbac said:
ovens, stove tops, insta hot water heater, I am not refering to the ocpd

Do they have ON/OFF switches?
Cord connections?

These are appliances....check Part III of 422 [starting at 422.30 ~ '05]
 