Here is the situation:
200 amp, underground 3 wire service to a residence.
3 wires from the street land in a disconnect.
Greenfield with 3 conductors go from the disconnect to the main breaker panel.
Each end of the greenfield has a grounding bushing wtih #8 solid under the set screw to the ground bus in the respective box.
Another #4 copper wire (THHN) not in the greenfield is routed from disconnect ground bus to main breaker panel ground bus.
Must there be a ground in the greenfield from disconnect to main breaker panel?
This is an existing install at a home that is for sale and the AHJ is saying a ground wire must be installed IN the greenfield.
He has not supplied any code reference yet....
Thank you.