You have feeders after the first disc
There is about 3' of flex from the meter to the disconnect.
Then there is about 7' (maybe 8') of flex from the disconnect to the MB panel.
I don't see how the exception fits the OP's situation. I still say he has a violation of 250.102(E).It starts out saying it cannot be longer than 6' if on the outside. then,,,IMO,,,the first exception after (e) allows you to do this, if he removed the bonding bushing jumper,(discard it) and landed the EBJ in the bushing, would meet the exception and be allowed to be longer than 6 ft and be on the outside.
Hi Dennis;
Sorry for the confusion.
Meter is on the house.
First run of flex is 3 or 4' from the back of the meter pan into the disconnect.
Then there is about 7' to 8' of flex from the disconnect to the main breaker panel.
The run to main breaker panel only has 3 conductors in it, with the ground run as a seperate conductor from disconnect to main breaker panel.
I appreciate all of your input. I expect to speak with the inspector tomorrow. I will update if I get some code references from him.
Till tomorrow.
Joe -- look at article 230.43 (15). The flex cannot be over 6'
(15) Flexible metal conduit not over 1.8 m (6 ft) long or liquidtight flexible metal conduit not over 1.8 m (6 ft) long between raceways, or between raceway and service equipment, with equipment bonding jumper routed with the flexible metal conduit or the liquidtight flexible metal conduit according to the provisions of 250.102(A), (B), (C), and (E)
Joe -- look at article 230.43 (15). The flex cannot be over 6'
230.43(15) Flexible metal conduit not over 1.8 m (6 ft) long or liquidtight flexible metal conduit not over 1.8 m (6 ft) long between raceways, or between raceway and service equipment, with equipment bonding jumper routed with the flexible metal conduit or the liquidtight flexible metal conduit according to the provisions of 250.102(A), (B), (C), and (E)
Denis,
Sounds like 240.33 is saying that the service conductors cannot be routed in the flex longer than 6'.
The conductors from the meter to the disconnect are service conductors.
Are the conductors from the disconnect to the main breaker panel service conductors or feeders?
There is about 3' of flex from the meter to the disconnect.
Then there is about 7' (maybe 8') of flex from the disconnect to the MB panel.
Hi Dennis;
Sorry for the confusion.
Meter is on the house.
First run of flex is 3 or 4' from the back of the meter pan into the disconnect.
Then there is about 7' to 8' of flex from the disconnect to the main breaker panel.
The run to main breaker panel only has 3 conductors in it, with the ground run as a seperate conductor from disconnect to main breaker panel.
I appreciate all of your input. I expect to speak with the inspector tomorrow. I will update if I get some code references from him.
Till tomorrow.
300.3(B)(2) allows an equipment bonding jumper to be installed outside the raceway. The conductor in question is an equipment grounding conductor and not an equipment bonding conductor. I don't see any provisions that permit this EGC to be run outside the raceway....
300.3(B) Says all conductors of a circuit including equipment grounding conductors must be run within the same raceway or cable.
300.3(B)(2) allows you to run on the outside of the raceway if it done in accordance to 250.102(E)
...
300.3(B)(2) allows an equipment bonding jumper to be installed outside the raceway. The conductor in question is an equipment grounding conductor and not an equipment bonding conductor. I don't see any provisions that permit this EGC to be run outside the raceway.
Bonding Jumper, Equipment. The connection between two or more portions of the equipment grounding conductor.
I agree that I don't see a reason to ever install an equipment bonding conductor on the outside of the raceway. Exhibit 2.46 in the handbook shows the use of an equipment bonding jumper in place of the code required EGC. I see no provision in the code that lets you use an equipment bonding jumper in place of an EGC. There are a lot of issues with the code terms in Article 250 that make the use of that article much more difficult than it should be.OK, so what is the difference between an equipment grounding conductor and an equipment bonding jumper? If you run it through a raceway how is it a bonding jumper and not an equipment grounding conductor when they both appear to serve the same purpose in this case. About the only thing that comes to mind that I would call an equipment bonding jumper over calling it an equipment grounding conductor is a conductor connected to a bonding bushing, or other similar device. I dont know why I would ever have a need to install this on the outside of a raceway.
Thank you all for the repoonses.
I did speak with the inspector on the phone.
He did NOT specifiy any NEC code articles.
I suggested that 250.102(E) addresses this situation and that in fact the flex is longer than 6'.
We also discussed the fact that this was inspected and PASSED in Aug 2005. He double checked the records at his office and yes, it was passed in 2005.
He is discussing with the construction official and will get back to me next week.
The inspector said that maybe it will be left as it is...
Thank you all for the repoonses.
I did speak with the inspector on the phone.
He did NOT specifiy any NEC code articles.
I suggested that 250.102(E) addresses this situation and that in fact the flex is longer than 6'.
We also discussed the fact that this was inspected and PASSED in Aug 2005. He double checked the records at his office and yes, it was passed in 2005.
He is discussing with the construction official and will get back to me next week.
The inspector said that maybe it will be left as it is...