Do you need to allow for the working space in 110.26 for a non fused safety switch?
 
Specifically for a disconnect for an AC drycooler?
This is a 480 volt nonfused disconnect. (not a disco)
This would be a condition 2 that would require 3'6" of clearance.
 
I believe that it needs the proper clearance and headroom.
	
		
			
		
		
	
				