So, its a suburb of \\Chicago, Lombard IL. my question is:
I have a 20 amp circuit to run, I want to run it through a pullout 30 Amp A/C disconnect box, COMPLETELY separate from the 30 amps - I do not want to tap....I want to run it through the 3/4 that only has 2 # 10s from the panel, to get out of basement, around a corner - that puts me 10 feet away from where I need to be. Then, splice the 12s in the A/c disconnect box, and run a 1/2 rigid off their disconnect box through its 1/2 KO...Can I do this, I looked all over 430 and can't find a yes or no.....
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
One possible issue is if the AC conductors are already operating at or near their maximum ampacity and now you need to derate them to 80%.
 