III. Disconnecting Means
690.13 All Conductors. Means shall be provided to disconnect
all current-carrying dc conductors of a photovoltaic system
from all other conductors in a building or other structure.
A switch, circuit breaker, or other device shall not be installed
in a grounded conductor if operation of that switch, circuit
breaker, or other device leaves the marked, grounded conductor
in an ungrounded and energized state.
Exception No. 1: A switch or circuit breaker that is part of
a ground-fault detection system required by 690.5, or that
is part of an arc-fault detection/interruption system required
by 690.11, shall be permitted to open the grounded
conductor when that switch or circuit breaker is automatically
opened as a normal function of the device in responding
to ground faults.
Exception No. 2: A disconnecting switch shall be permitted
in a grounded conductor if all of the following conditions
are met:
(1) The switch is used only for PV array maintenance.
(2) The switch is accessible only by qualified persons.
(3) The switch is rated for the maximum dc voltage and
current that could be present during any operation,
including ground-fault conditions.
Informational Note: The grounded conductor may have a
bolted or terminal disconnecting means to allow maintenance
or troubleshooting by qualified personnel.