Disconnect for Instant hot for pantry sink

Purr24

Member
Location
Pennsylvania
Occupation
Electrician
Can I install a disconnect above a drop ceiling that serves for a 30 amp 208v 1/phase instant hot? Is this legal? Under the sink is congested with plumbing and a sewage pump. Breaker box is not with in site for breaker lock. Thoughts
 

rc/retired

Senior Member
Location
Bellvue, Colorado
Occupation
Master Electrician/Inspector retired
Can I install a disconnect above a drop ceiling that serves for a 30 amp 208v 1/phase instant hot? Is this legal? Under the sink is congested with plumbing and a sewage pump. Breaker box is not with in site for breaker lock. Thoughts
If the insta-hot is above the sink ceiling, I would be ok with the disconnect being up there.
I'm under the impression that the reason for a breaker lock is because the panel is not within sight.

Ron
 