wwhitney
Senior Member
- Location
- Berkeley, CA
- Occupation
- Retired
For the schematic in post #6, isn't the question of whether the red control circuitry qualifies as a disconnect (it doesn't) moot, because the two branch circuit breakers in the upper left qualify if readily accessible?
That assumes the "breakers" in the control panel are supplementary OCPD and not the branch circuit breakers. If they are the branch circuit breakers, then they would need to be readily accesible.
Cheers, Wayne
That assumes the "breakers" in the control panel are supplementary OCPD and not the branch circuit breakers. If they are the branch circuit breakers, then they would need to be readily accesible.
Cheers, Wayne