NFPA70 Section 404.8 calls for a maximum height above the floor for a disconnect of 79 inches but provides for an exception (#2):
"Switches and circuit breakers installed adjacent to motors, appliances and other equipment they supply shall be permitted to be located higher than 2.0m (6ft 7 in) and to be accessible by portable means."
Now, I am installing a 2 door disconnect enclosure that has a nominal disconnect height of 68 inches above the floor - this is defined by the flange opening on the enclosure. The problem is that the enclosure is being installed on a houskeeping pad some 15" high. The disconnect will only be used when the system requires a full power down for electrical maintenance
Does anyone out there think that I will have any problems with this installation?
"Switches and circuit breakers installed adjacent to motors, appliances and other equipment they supply shall be permitted to be located higher than 2.0m (6ft 7 in) and to be accessible by portable means."
Now, I am installing a 2 door disconnect enclosure that has a nominal disconnect height of 68 inches above the floor - this is defined by the flange opening on the enclosure. The problem is that the enclosure is being installed on a houskeeping pad some 15" high. The disconnect will only be used when the system requires a full power down for electrical maintenance