What definition?Look at the definition in Article 100.
Wow confusing like many of the NEC requirements...I'll get back to you on the equipmentProbably the breakers within sight can be your disconnects. But requirements for disconnects depend on the equipment and vary by whichever Article of the code applies to the equipment. You may not even need disconnects within sight. So what is the equipment?
Yeah that was a good question actually. It's 'In Sight From' as Sue mentioned. And not cross referenced at 'Within ..." even though the latter phrasing is used more often in the code.What definition?
It was relocated to 110.29 because the specification of not more than 50' was read as a requirement and definitions are not permitted to contain requirements.What definition?
110.29 In Sight From (Within Sight From, Within Sight).
Where this Code specifies that one equipment shall be “in sight from,” “within sight from,” or “within sight of” another equipment, the specified equipment shall be visible and not more than 15 m (50 ft) distant from the other.