Recently the facility I work in is installing a large number of new CNC based equipment. This equipment requires 200-220Volt 3 Phase power.
The plant I work in has 480 Volt 3-Phase,(supplied through a buss system 18 feet above the floor). A transformer was purchased to be installed with each of the CNC units.
The transformers are (45KW) are bolted to the floor next to the CNC equipment. One Transformer supplies a single piece of equipment. On the first 4 machines a disconnect switch was installed between the 480V buss and the transformer.
Now our divisional engineers want to eliminate the disconnect switches installed between the 480V buss and the transformers. They have stated that there is nothing in the NEC that requires a disconnect, in this case.
I am curious if this type of installation has been directly addressed in the code. I have not been able to find a definitive argument against the policy they want to adopt at this location.
Personally I have stated to the engineers that the disconnects should be installed because I would consider the transformer as part of the equipment since it is needed to derive the correct operating voltage. Of course they want to see where it is required in the code.
Any comments on this type of installation would be appreciated.
The plant I work in has 480 Volt 3-Phase,(supplied through a buss system 18 feet above the floor). A transformer was purchased to be installed with each of the CNC units.
The transformers are (45KW) are bolted to the floor next to the CNC equipment. One Transformer supplies a single piece of equipment. On the first 4 machines a disconnect switch was installed between the 480V buss and the transformer.
Now our divisional engineers want to eliminate the disconnect switches installed between the 480V buss and the transformers. They have stated that there is nothing in the NEC that requires a disconnect, in this case.
I am curious if this type of installation has been directly addressed in the code. I have not been able to find a definitive argument against the policy they want to adopt at this location.
Personally I have stated to the engineers that the disconnects should be installed because I would consider the transformer as part of the equipment since it is needed to derive the correct operating voltage. Of course they want to see where it is required in the code.
Any comments on this type of installation would be appreciated.