Is there a requirement to disconnect all the conductors including the neutral conductor to a trailer, mobile home etc?? Ive searched the code but couldnt find any.
480sparky said:I thought the grounded was the neutral, hots are ungrounded.....![]()
On a grounded system one of the service entrance conductors is the grounded conductor and there must be a means of disconnect. However you are not required to provide a disconnect switch for the grounded conductor.230.70 General.
Means shall be provided to disconnect all conductors in a building or other structure from the service-entrance conductors.
230.75 Disconnection of Grounded Conductor.
Where the service disconnecting means does not disconnect the grounded conductor from the premises wiring, other means shall be provided for this purpose in the service equipment. A terminal or bus to which all grounded conductors can be attached by means of pressure connectors shall be permitted for this purpose. In a multisection switchboard, disconnects for the grounded conductor shall be permitted to be in any section of the switchboard, provided any such switchboard section is marked.
Only the ungrounded.brother said:Is there a requirement to disconnect all the conductors including the neutral conductor to a trailer, mobile home etc?? Ive searched the code but couldnt find any.
brother said:Is there a requirement to disconnect all the conductors including the neutral conductor to a trailer, mobile home etc?? Ive searched the code but couldnt find any.