If they want a disco outside at the generator. Can't you count the gas shut off at the generator as a disco? Kill the fuel kill the generator.
Why would any inspector not consider the breaker "Readily Accessible" located on the side of a generator? Think about this before you answer...Main panel in a house has a door covering the breakers...its readily accessible...but we place a door on a generator and its not the same? I think the OHJ should want to see the door as you approuch it not hide it around the back of the generator....it's just common sense. I would think that anyone having the skills & knowledge ...article 100 qualified person... If you have the skill & knowledge you should know there is a breaker behind that door just like on the panel.
There is no doubt in my mind the generator companies placed that breaker there as a means of service disconnect..not because they had some extra breakers laying around
IMO...I think AC units should have the same disconnect mounted with in the unit just like the generator has.
Just what ever one would want, electricity going through your body while you wait for the gen. to run out of gas:happysad:If they want a disco outside at the generator. Can't you count the gas shut off at the generator as a disco? Kill the fuel kill the generator.
I think that you can if the gen. shuts down immediately.If they want a disco outside at the generator. Can't you count the gas shut off at the generator as a disco? Kill the fuel kill the generator.
225.31 Disconnecting Means. Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure. The disconnect located inside this generator does not fulfill the requirements of 702.12 as it is not within sight when the lid is closed. The disconnect must meet the requirements of 225.36 in that it must be suitable as service equipment and disconnect all ungrounded conductors The disconnect located inside a locked generator is readily accessible just like the service disconnect located in the panel in my basement which has a locked door and most other service disconnects throughout this great nation are located behind locked doors. What it does not meet is the within sight part due to being under a closed lid unless there is a window so that the disconnect is visible with the lid closed. In the event that the disconnect on the generator is not within sight with the lid closed then one must be installed at the building that complies with Part II of Article 225. 702.12 states that even if the generator disconnect is visible and readily accessible it must comply with 225.36 and be suitable for service equipment. When I am in doubt of the rating of a disconnect as being ?suitable as service equipment? I generally look at Parts V, VI, and VII of 230 for a better understanding of suitable as service equipment. Yes this would be acceptable as long as the gas valve is suitable as service equipment, see 702.12 Why is a 200 amp transfer being installed on a 20KW generator? 20k/240=83 amps :? |
Probably because that's the way the mfr's are packaging them. Generac is selling 20K units with 100 or 200A service rated xfer switches.702.12 Outdoor Generator Sets.
Why is a 200 amp transfer being installed on a 20KW generator? 20k/240=83 amps :?
702.12 Outdoor Generator Sets.
Where an outdoor housed generator set is equipped with a readily accessible disconnecting means located within sight of the building or structure supplied, an additional disconnecting means shall not be required where ungrounded conductors serve or pass through the building or structure. The disconnecting means shall meet the requirements of 225.36.
(Read only the underlined parts)
225.36 Suitable for Service Equipment.
The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
225.31 Disconnecting Means.
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
The disconnect located inside this generator does not fulfill the requirements of 702.12 as it is not within sight when the lid is closed.
The disconnect must meet the requirements of 225.36 in that it must be suitable as service equipment and disconnect all ungrounded conductors
The disconnect located inside a locked generator is readily accessible just like the service disconnect located in the panel in my basement which has a locked door and most other service disconnects throughout this great nation are located behind locked doors. What it does not meet is the within sight part due to being under a closed lid unless there is a window so that the disconnect is visible with the lid closed.
In the event that the disconnect on the generator is not within sight with the lid closed then one must be installed at the building that complies with Part II of Article 225.
702.12 states that even if the generator disconnect is visible and readily accessible it must comply with 225.36 and be suitable for service equipment. When I am in doubt of the rating of a disconnect as being “suitable as service equipment” I generally look at Parts V, VI, and VII of 230 for a better understanding of suitable as service equipment.
Yes this would be acceptable as long as the gas valve is suitable as service equipment, see 702.12
Why is a 200 amp transfer being installed on a 20KW generator? 20k/240=83 amps :?
B) Grounding.
Where removal of a grounding or bondingconnection in normal power source equipment interrupts thegrounding electrode conductor connection to the alternatepower source(s) grounded conductor, a warning sign shall beinstalled at the normal power source equipment stating:WARNINGSHOCK HAZARD EXISTS IF GROUNDINGELECTRODE CONDUCTOR OR BONDING JUMPERCONNECTION IN THIS EQUIPMENT IS REMOVED
WHILE ALTERNATE SOURCE(S) IS ENERGIZED
I'm trying to think of a reason / instance when you would disconnect a ground when the generator is running?
Wow!! This may be a first, Mike. I fully agree with your comments.702.12 Outdoor Generator Sets.
Where an outdoor housed generator set is equipped with a readily accessible disconnecting means located within sight of the building or structure supplied, an additional disconnecting means shall not be required where ungrounded conductors serve or pass through the building or structure. The disconnecting means shall meet the requirements of 225.36.
(Read only the underlined parts)
225.36 Suitable for Service Equipment.
The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
225.31 Disconnecting Means.
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
The disconnect located inside this generator does not fulfill the requirements of 702.12 as it is not within sight when the lid is closed.
The disconnect must meet the requirements of 225.36 in that it must be suitable as service equipment and disconnect all ungrounded conductors
The disconnect located inside a locked generator is readily accessible just like the service disconnect located in the panel in my basement which has a locked door and most other service disconnects throughout this great nation are located behind locked doors. What it does not meet is the within sight part due to being under a closed lid unless there is a window so that the disconnect is visible with the lid closed.
In the event that the disconnect on the generator is not within sight with the lid closed then one must be installed at the building that complies with Part II of Article 225.
702.12 states that even if the generator disconnect is visible and readily accessible it must comply with 225.36 and be suitable for service equipment. When I am in doubt of the rating of a disconnect as being ?suitable as service equipment? I generally look at Parts V, VI, and VII of 230 for a better understanding of suitable as service equipment.
Yes this would be acceptable as long as the gas valve is suitable as service equipment, see 702.12
Why is a 200 amp transfer being installed on a 20KW generator? 20k/240=83 amps :?
Wow!! This may be a first, Mike. I fully agree with your comments.