It looks like you must provide a disconnect switch.630.13 Disconnecting Means.
A disconnecting means shall be provided in the supply circuit for each arc welder that is not equipped with a disconnect mounted as an integral part of the welder.
The disconnecting means shall be a switch or circuit breaker, and its rating shall not be less than that necessary to accommodate overcurrent protection as specified under 630.12.
I have some Meltric plugs in my truck and I like them. I also know that they are rated for use as a disconnect.Originally posted by plugman:
There is a device on the market that would serve as both a plug and receptacle and a switch rated disconnect and allow you to be code compliant.
Originally posted by iwire:...
In this instance the requirement specifically states disconnect switch it does not say disconnect receptacle
...
Bob,Disconnecting Means . A device, or group of devices, or other means by which the conductors of a circuit can be disconnected from their source of supply.
Switch: A device for opening and closing or for changing the connection of a circuit. In these rules, a switch is understood to be manually operable, unless otherwise stated.
(NESC/T&D) (2-1997, C2.2-1960)