disconnect switch and lug only panel
sangkim0707
NYC
hello forum
one of our job site has (1) main disconnect switch and (2) main lug only panel fed from the disconnect switch
I am not sure if i have to change the (2) panels to Main breaker type panel
The disconnect switch and panels are right next to each other within 6'
Its in NYC
any idea??
Thank you!
Is this main disconnect just a switch or is it a panel with a main breaker? Explain a bit more
[MENTION=160285]sangkim0707[/MENTION]
It sounds like you are using the tap rule so article 240.21 would come into play. You will need a breaker if the conductors off the switch are smaller than the line side. If the conductors are the same size as the main feed to the disconnect then I don't believe you would need a main.
Is this main switch attached to the structure where the panels are and is it being fed from a breaker? Lots of questions and the answers may change the response.
BTW, You are still a moderated member so it may take a bit of time for your post to appear. This will change soon
D/S - fused disconnect switch 3P 400A
Panels - 200A 3P 120/208Y each
its in same room but exact distance is about 9ft i just measured it
i did not open the wire through box thats feeding both of the panel
but i am sure the wire (conductor size) is smaller than feeding D/S or going into the wire through
probably double lugged inside
400 amp fuse protecting a 200 amp MLO panel would be a violation of 408.36
also can anyone educate me with distance rules between disconnecting means (over-current protection) to the circuit panels or loads?