Ask him to talk to mom when the motor grinds up the child that walked into the area while he was reconnecting the machine. That's why the it includes "and the driven equipment" as well as the motor. You got to turn that thing back on once you get it fixed.
pf, mk -
First, a disclaimer: I don't build or design carwashes. So maybe there is sneaky, dangerous stuff going on that I don't know about - and I'm all wet:roll:
Let's think about this a minute.
If you put in a disconnect, the code requires it to be, "in sight from the motor location and driven machinery location". The few times I've put them in they were right next to the motor and yes you could see the driven machinery.
So, the operator gets an emergency and runs down to the end of the conveyor and shuts off the motor disconnect. Not a good idea. Especially if there is more than one disconnect and the operator, in a panic, grabs the wrong one.
So, here is my design (carwash ignorant person that I am):
The operator gets an emergency and reaches out and slaps the E-stop button - all the conveyors/pumps/driven machinery immediately stops. No waiting for the operator to run to the other end. No finding multiple disconnects to stop all of the machinery.
But wait, suposing the operator is on the other side - okay I'll put a butt in over there as well. But wait, the operator can be any where along this area - okay, Ill put up a pull rope.
There are a lot better ways than a disconnect switch to provide for general safety shutdown.
Please note I'm not suggesting to not install a disconnect. If the install does not meet 430.102.B Exception, the put in the disconnect. I just would not count on it for a general safety shutdown - that's what the E-stops are for.
cf