electrofelon
Senior Member
- Location
- Cherry Valley NY, Seattle, WA
From other threads i've been on, if you use current limiting fuses to protect a downstream breaker panel, that combo has to be series rated. dynamic impedance from the breakers will cause the CL fuses to behave differently from what you see on their let-thru charts, so you have no control or idea of how the system as a whole will behave... so that forces a series rating listing needed between the fuses and the downstream breaker panel, since it's something that the manufacturer can study. At least that's what i've read.
I dont think you have it quite right. Perhaps what people were trying to say, or what you were told but misinterpreted, is that you cannot use CL fuses to reduce the AFC downstream, at least based on manufacturer charts. You are basically stuck with whatever tested series combination there is. For the most part just ignore the concept of a CL fuse. Really the only exception is under engineering supervision, and from what I hear, good luck getting an EE to stamp a non tested series combination.