Hey guys,
If you look at the attachment, I'm trying to understand the table with the heavy duty switches, towards the middle. Let's say I choose an 800 amp switch, in a NEMA 1 enclosure. I'll use either class R, J, or T fuses, as noted on top of the table.
The short circuit ratings of the switch are as follows:
200k at 480V
100k at 600V
My question is: does the table mean I can't use a fuse rated for 250 volts? The fuses have to be rated either rated for 480 or 600 volts? I'm looking to use the switch on a 120/208 volt system.