Hey guys,
Revisiting this thread. Is it possible to fit 600 volt rated fuses on a 240 volt rated disconnect switch / distribution board with disconnect switches? are there adaptors available?
 
If you have a 240V disconnect switch, you must have 240V, not 480 or 600. So why would you be using 600V rated fuses? Do you like spending extra money needlessly?

The point is that no, you will not find an "adaptor" to do this because nobody would be doing this.
 
Hey guys,
Revisiting this thread. Is it possible to fit 600 volt rated fuses on a 240 volt rated disconnect switch / distribution board with disconnect switches? are there adaptors available?
No adapter is available.
UL Listing requires 600V fuses to be built larger than 240V so they can not be interchanged.
 