I'm confused. :confused: Why would a 120 volt machine need a 3-pole disconnect? But to answer (what I think is) your question, you cannot switch the neutral. Yes, 404.2(B) applies.
 
Re: Disconnect

The exception to 404.2(B) will permit the grounded conductor to be opened by the disconnect.
Don
 
Re: Disconnect

its not unusual to see a 120V device with a three pole disconnect. you just don't use all the poles.

I might be inclined to wire the neutral through the disconnect in such a case.

[ August 16, 2005, 11:30 AM: Message edited by: petersonra ]
 
Re: Disconnect

I wouldn't; I'd take the 3-phase switch and replace it with a single-pole one, and keep the 3-pole one for when I need it.
 