Disconnecting means for a mobile home feeder?

sw_ross

Senior Member
Location
NoDak
I’m trying to locate the requirements for the location of the disconnecting means for a mobile home? Specifically the distance requirement. I looked in 550 but didn’t have any luck.
I know it’s something like “adjacent to but not more than 25 feet” or some distance like that.
Thanks in advance for steering me in the proper direction!
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
550.32 Service Equipment.
(A) Mobile Home Service Equipment. The mobile home service
equipment shall be located adjacent to the mobile home
and not mounted in or on the mobile home. The service
equipment shall be located in sight from and not more than
9.0 m (30 ft) from the exterior wall of the mobile home it
serves. The service equipment shall be permitted to be located
elsewhere on the premises, if a disconnecting means suitable
for use as service equipment is located within sight from and
not more than 9.0 m (30 ft) from the exterior wall of the
mobile home it serves and is rated not less than that required
for service equipment in accordance with 550.32(C). Grounding
at the disconnecting means shall be in accordance with
250.32.
 