We are working on an estimate for a water treatment plant, and the bid documents show some meduim voltage motors (4160 volts) for pumps that are being fed from gear located in another room (not with in sight). My problem is that the Bid Documents do not show any disconnecting means in the pump room for these motors.
I have looked at NEC 430-102 B (1) exception for guidance and it appears that you wouldn't need a disconnecting means to be located in the same room if situation meets the requirements of the exception.
If this is the case, then the MCC that is serving the motors (which is located in the other room) would need to be permantely capable of being locked-out in the "open" position. Would this satisfy the requirement.
The main thing is that if I included disconnecting means for the motors in the pump room, (which would be required to have a 316 steel enclosure) in my estimate, I will probably be un-successful in the bidding process. Since we are working off of bid documents, and not construction documents I feel that I should "estimate" only what is show on the drawings.
Is this a bad practice?
I have looked at NEC 430-102 B (1) exception for guidance and it appears that you wouldn't need a disconnecting means to be located in the same room if situation meets the requirements of the exception.
If this is the case, then the MCC that is serving the motors (which is located in the other room) would need to be permantely capable of being locked-out in the "open" position. Would this satisfy the requirement.
The main thing is that if I included disconnecting means for the motors in the pump room, (which would be required to have a 316 steel enclosure) in my estimate, I will probably be un-successful in the bidding process. Since we are working off of bid documents, and not construction documents I feel that I should "estimate" only what is show on the drawings.
Is this a bad practice?