Disconnecting means for packaged equipment

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
We have an 480V air compressor - packaged equipment-with no local disconnecting means but there’s a lockable disconnect switch upstream approximately 200 feet away, out of sight of the skid—as I recall this is sufficient and a local disc is not required… comments


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If there is a motor controller involves you must have a disconnect within sight from and not more than 50 ft from.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
If there is a motor controller involves you must have a disconnect within sight from and not more than 50 ft from.

Right, but the controller is on the skid. So the motor is within sight of the controller


Sent from my iPhone using Tapatalk
 