Can a disconnecting means such as a circuit breaker for a 120vac space heater be out of sight if it is lockable in the open position similar to 430.102?
I should have clarified; the space heater is located within a Nema 7, combination motor starter installed in a CID2 area - on a switchrack. I was looking at sections 430.113 and 110.25 and it looks like an external disconnect is not required as long as the upstream branch CB is lockable.
Thanks to all.