Disconnecting means for space heaters

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
Can a disconnecting means such as a circuit breaker for a 120vac space heater be out of sight if it is lockable in the open position similar to 430.102?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
If you are referring to fixed electric space heating (such as baseboard heat or such), there are a lot of details to consider. See 424.19-424.21.
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
I should have clarified; the space heater is located within a Nema 7, combination motor starter installed in a CID2 area - on a switchrack. I was looking at sections 430.113 and 110.25 and it looks like an external disconnect is not required as long as the upstream branch CB is lockable.
Thanks to all.
 