Hey, fellas. Trying to see everyone's thoughts on this topic:
There is a 4,160V chiller at an industrial facility. It has a remote across-the-line starter with a disconnect that is in a different room than the chiller, and there is no additional means of disconnect at the chiller itself. Can this be justified with exceptions?
440.14 implies there may be an exception if this chiller is used for an industrial process at a facility with written safety procedures, but that exception (No. 1) also references back to 430.102(A) which deals with motor controllers, not the equipment itself.
I read this as, in no case, shall the ACR equipment itself have a disconnecting means that is not within sight and readily accessible. I don't see an exception to the rule, but I'm not 100% sure of the intent of 440.14 (Exception No. 1). Why have that exception at all if it would only apply to a controller and not the equipment itself?
There is a 4,160V chiller at an industrial facility. It has a remote across-the-line starter with a disconnect that is in a different room than the chiller, and there is no additional means of disconnect at the chiller itself. Can this be justified with exceptions?
440.14 implies there may be an exception if this chiller is used for an industrial process at a facility with written safety procedures, but that exception (No. 1) also references back to 430.102(A) which deals with motor controllers, not the equipment itself.
I read this as, in no case, shall the ACR equipment itself have a disconnecting means that is not within sight and readily accessible. I don't see an exception to the rule, but I'm not 100% sure of the intent of 440.14 (Exception No. 1). Why have that exception at all if it would only apply to a controller and not the equipment itself?