gajones2

New member
Location
Wisconsin
In an industrial facility, are disconnects required to be within line of sight of the device they are disconnecting? It is my understanding that if the disconnect is lockable it is not required to be in line of sight.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Disconnects

If you don't have a written lock out procedure and "quailfied" maintenance personel, you must have a disconenct within sight of the equipment.