G gajones2 New member Location Wisconsin Mar 25, 2003 #1 In an industrial facility, are disconnects required to be within line of sight of the device they are disconnecting? It is my understanding that if the disconnect is lockable it is not required to be in line of sight.
In an industrial facility, are disconnects required to be within line of sight of the device they are disconnecting? It is my understanding that if the disconnect is lockable it is not required to be in line of sight.
russ Senior Member Location Burbank IL Mar 25, 2003 #2 Re: Disconnects I believe 430.102 is what your looking for. Russ
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Mar 25, 2003 #3 Re: Disconnects If you don't have a written lock out procedure and "quailfied" maintenance personel, you must have a disconenct within sight of the equipment. Don