Discontinued westinghouse breakers

Status
Not open for further replies.

mdbb12

Member
I am currently working on a project that has a 1200A magnetic trip HNB frame Westinghouse breaker that is discontinued. It has three adjustments I am assuming they are long time, short time and instantaneous. Can any one clarify this?
 
HNB

HNB

That breaker has magnetic-only adjustability, from 3.4 to 6.7X the trip rating. That's according to the SKM library file.
 
They are all the same. One dial is for A-phase, one for B, and the third for C phase. They should all be set to the same value.
 