tryinghard
Senior Member
- Location
- California
NO - A duplex is two recepts, the total for both would be 16A. See table 210.21(B)(2)
I just spun out; and I want to see it as you do, but if I have 10A in one recept and 7 in the other where in 210.21(B)(2) is "both" stated. A recept cannot have more than 16A plugged into it and it wouldn't. Like I said I just spun out [UGH]