Re: dishwasher and disposal
Originally posted by dana1028:
JW - what about this section? ..."or the marked rating of an appliance having combined loads as provided in 422.62."
422.62. Where a motor-operated appliance nameplate includes a HP rating, the rating shall not be less than the HP rating on the motor nameplate....calculated per 430.110(C)(1).
There are a few articles that need to be look at closely when addressing a dishwasher. First being 430.6 due to the fact that the dishwasher has a motor. Here we are told to look at 422 this dishwasher being an appliance as shown here.
430.6 (A)(1) Exception No. 3: For a listed motor-operated appliance that is marked with both motor horsepower and full-load current, the motor full-load current marked on the nameplate of the appliance shall be used instead of the horsepower rating
In 422.10 (A) we are told that the branch circuit is not to be less that the appliance and any combination of loads in that appliance such as the motor and the heater for the water.
422.10 (A) Individual Circuits. The rating of an individual branch circuit shall not be less than the marked rating of the appliance or the marked rating of an appliance having combined loads as provided in 422.62.
The rating of an individual branch circuit for motor-operated appliances not having a marked rating shall be in accordance with Part II of Article 430.
422.10 tells us to look at 422.62 when there is a marked rating on the appliance and go to 430 when there is no marked rating. Most dishwashers have a label as well as a manual so let?s look at 422.62.
422.62 (B) Additional Nameplate Markings. Appliances, other than those factory-equipped with cords and attachment plugs and with nameplates in compliance with 422.60, shall be marked in accordance with 422.62(B)(1) or (B)(2).
(1) Marking. In addition to the marking required in 422.60, the marking on an appliance consisting of a motor with other load(s) or motors with or without other load(s) shall specify the minimum supply circuit conductor ampacity and the maximum rating of the circuit overcurrent protective device.
This requirement shall not apply to an appliance with a nameplate in compliance with 422.60 where both the minimum supply circuit conductor ampacity and maximum rating of the circuit overcurrent protective device are not more than 15 amperes.
I separated this section for clarity of the second part. (This requirement shall not apply to an appliance with a nameplate where both the supply conductor and the overcurrent protective device are not more than 15 amperes.)
The manufacture?s label on the dishwasher that I posted earlier stated that the dishwasher was to be supplied with a 15 amp circuit. Therefore should this dishwasher be supplied with a 20 amp OCPD and have no disposal it would be in violation of 422.62 and 110.3(B).
Edited to change 433.62 to 422.62. Thanks Eric
[ October 01, 2005, 08:29 PM: Message edited by: jwelectric ]