e57
Senior Member
- Location
- San Francisco, CA
(1)Typical to all MWBC's (Muilti-Wire Branch Circuits) the ? (hot) conductors are on different legs - either opposite eachother on a split phase system 240/120 (typical to most dwellings), or 120 degrees from each other in the case of 3 phase 208/120 power in many multi-family or high rise buildings. And so the current on the neutral will be the imbalanced portion of the circuit. (In a perfect world) If you had 10A on one leg, and 10A on the other of the circuit (240/120) there would be ZERO amps on the neutral. In your case, of 8.1, and 12A - the difference is 3.9A, and that is what the neutral amperage would be when both units are operating at full load.E57,
This is a two part question:
1) First my setup: Both the dishwasher and disposal are cord connected on a duplex receptacle with the tab broken sharing the neut. from 12/3 feed from panel with 2 pole 20A OCPD.
Dishwasher: Eurotech = 12A
Disposal: Insinkerator = 8.1A
When trying to figure the loads for this setup I am somewhat confused from the earlier posts on this thread. If 12/3 has been ran as stated above, the two above amperages are not additive making it 20.1A but on separate 20A circuits with that 2 pole circuit breaker.
~~
2) ~Is the two pole breaker acting like two separate 20A breakers for two separate circuits?
Thanks,
Mka
However, when only one item is on - the neutral current would match whatever that item is. So the neutral current when ONLY the garbage disposal is on by itself would be 8.1... (as it would be in a 2-wire circuit)
(2)Yes the breaker acts as two seperate breakers, and the handle tie ensures that both are disconnected at the same time.