What was I thinking, who needs to be able to disconnect the power to a commercial DW? :roll:
iwire said:What was I thinking, who needs to be able to disconnect the power to a commercial DW? :roll:
Dennis Alwon said:What about a lockout on the breaker.
iwire said:What about it?
That section is right above the section that says accessible.
So yes it can be behind that front cover, but once you open that cover you have to be able to access the outlet without pulling out the DW.
acrwc10 said:Who says that it is not accessible if it is behind the unit,
iwire said:A disconnecting means that can not be accessed is useless.
iwire said:In my opinion the inspector can.
Accessible (as applied to equipment) Admitting close approach; not guarded by locked doors, elevation, or other effective means.
IMO a inspector could say that having to remove the DW to 'access' the receptacle means that the receptacles placement does not allow 'close approach' and guards the receptacle by 'other effective means'.
A disconnecting means that can not be accessed is useless.
acrwc10 said:All I am saying is a plug behind the unit is not necessarily the only means to disconnect the unit.
I don't mean to throw a wrench into this thread but once you install those two screws isn't the unit considered to be "fixed in place" ? Also, bear in mind that in 422.16(B)(2) ALL 5 conditions have to be met. If anyone knows how to slide a dishwasher into a tight space with a 3'-4' cord and plug attached to it would you please post how you did it ?arcwc10 said:most dishwashers can be pulled out by removing 2 screws in the top front.
I always thought it was a good idea because I figured that the probability of there being an electrical issue would be far less than if there was a plumbing issue. Having a local disconnect means would make it safer for the plumber to service the unit. On the other hand, if one of us had to perform electrical service on the unit we would make damn sure that the power was turned off by any means possible. I can't say the same for plumbers. (And please, if any of you have dual licenses I didn't mean this as a personal attack - just observations over the years). And, if the disconnect means can't be readily accessible or within sight then the lock-out feature on the breaker (as Dennis suggested) is the best way to go IMHO (But that usually counts for squat !!!)I see receptacles behind the dishwasher frequently. Personally I think it is a bad place for it , but I don't see it as a violation of 422.16 B .