The pig draws 4.5 amps so no chance of overload. The #14 is the romex going to the receptacle under the sink. So what i have is a motor on #14. I know the hole setup violates nec but has worked fine for 11 years. I will in time likely fix it right. The place was built in 73 so has a few issues and i been fixing as time permits. I usually am over on what i install but this was something i just discovered while remodeling. This one of them i wont get paid type jobs.
Hmm, let's see..4.5 amps on a momentary load, the only part of the run (if I understand this correctly) is the run from the switch to the disposall receptacle, it has held up nicely for 11 years.
Table 310-16 lists 60deg C insulated 14 ga wire in a cable as 20 amps (if 90deg C it's 25 amps) with of course the Sec.240 reference for an OCPD of 15 amps.
What all this says to me is leave it alone! The downgraded OCPD is based on feed/home runs which would be subject to long-term loads and multiple devices in use, so this short piece to the disposall is one Code violation I wouldn't even lose sleep over.
There were (until inspectors caught on, correctly I will add) many homes wired with #14 switch legs with #12 feeds. Again, although a technical violation, from a REAL-WORLD viewpoint, not a latent fire hazard.