Distance between Pull Box, ocpd and site light?

Status
Not open for further replies.

pkelectrical

Member
Location
NJ
I can't remember if there is a code that requires you to install a pull box every so many feet. I need to install conduits for parking lots and some runs are 175'+ from OCPD to the site light. Need to pull #8 AWG. Was looking at 314.29 but nothing about the long distance.
 
I can't remember if there is a code that requires you to install a pull box every so many feet. I need to install conduits for parking lots and some runs are 175'+ from OCPD to the site light. Need to pull #8 AWG. Was looking at 314.29 but nothing about the long distance.

No rule on distance between pull boxes. but you are limited to 360 degrees of bends between pull boxes.

352.26 for PVC.
 
Last edited: