https://www.bicsi.org/uploadedFiles...entations/Caribbean/TIA-569UpdateOverview.pdf
TIA 569: "Non‐continuous supports located at intervals not to exceed 1.5 m (5 ft)"
As Hal wrote, this is not NEC code, but Telecom/Electronic Industries Association specs. I've always run any indoors type of Catx cable at 5' (or closer) supports. Hilti makes easy slide-in hangers that are wide and support a fair number of cables, but you could use L-clips shot or screwed to the deck with ceiling grid wire, superstrut, all-thread and Sammies, really anything (other than electrical conduit or sprinkler pipes :roll: ) to support the cable between trusses.
Here's a pic of the Hilti clips I've used before:
The top is good for probably 60 cables, the bottom is two clips locked together, each one good for about 20 cables. Keep in mind Cat 6 is fairly heavy and more sensitive to installation to certify; having high point loads on a bundle of cable because it's not supported right could cause a lot of problems.
Those pins are factory and made to be shot with a DX351 powder actuated tool w/clip attachment to concrete decking, but you can remove them and use screws for wood or sheet metal.