distance for SECs inside the building line

Status
Not open for further replies.

TimWA

Member
I'm stumped looking for the reference for unfused service entrance conductors no more than 15 ft. inside the building line?
 
Re: distance for SECs inside the building line

Good point, Mark.

Tim, if I understand your situation, you are about to take the Administrator exam. I suggest that if this subject comes up, you read the question very carefully. Be sure you understand whether they are asking about the NEC rule (no distance is specified) or the WAC rule (15 foot limit).

Also, be careful about whether they are talking about running the conductors into the building under the slab. So long as the conductors are below 2 inches of concrete, they are not yet "in the building." The 15 foot restriction begins when the conductors pop up from below the slab, even if they have travelled 200 feet under the concrete before they got to that point.
 
Re: distance for SECs inside the building line

Tim:
Make sure you have the current WAC rules.
You'll need the version effective June 30th 2005 and the admendment that goes into effect Nov 25th.
You need both. You can print them from the internet and take into the test with you.
Here is what I say in my classes for Washington State:
You can't know the NEC without knowing the WAC and vise versa....
Washington State does a great job of correcting the NEC mistakes for its rules.
 
Re: distance for SECs inside the building line

Wow - 15 FEET ? :eek: Here in Maryland I'm feeling lucky if they will approve 5 Feet ! I could have saved the customer over $600.00 on the last addition I did if the AHJ would have approved 8 Feet of unfused SE inside.
 
Re: distance for SECs inside the building line

really for 15 feet for unfused conductors for inside the resdential area is too much [ i am in state of wisconsin we are restricted to either 6 or 8 feet i useally go 2 meter {metric mesurement} anymore than that have to be fused for safety reason unless it is encasted in cement with pvc pipe.

i am not sure what other state will say about this for unfused conductors espcally in resdentinal area that part i feel it will related with NEC and state codes


Merci, Marc
 
Re: distance for SECs inside the building line

Originally posted by luckyshadow:
I could have saved the customer over $600.00 on the last addition I did if the AHJ would have approved 8 Feet of unfused SE inside.
You could run PVC and either brick it in or encase it in concrete. If you do that you can go as far as you want. It might be cheaper than the electric equipment.

See 230.6

[ November 18, 2005, 06:32 PM: Message edited by: iwire ]
 
Re: distance for SECs inside the building line

" You could run PVC and either brick it in or encase it in concrete.."
Not an option , Se running in basement, overhead in the joist's for the first floor. Had no choice but to set a 200 amp enclosed breaker then refeed the existing service making it a sub-panel
 
Re: distance for SECs inside the building line

Members of Forum,

I was just looking at "Versaroc" cement board,it is 71% Portland cement,10% fibers,etc.,also it is non-combustable.

So, keeping in line with this thread,I'm wondering if this product was built up to two inches around SE conductors entering the building would they be considered "outside". Just testing the "Edge".
 
Re: distance for SECs inside the building line

Depending on your location,the building codes may require only so many feet. Here it's 5ft.
If the structure makes this a problem the AJH will work with you. :p
 
Re: distance for SECs inside the building line

What we really need is for someone to manufacture a conduit that has a 2" concrete covering. Lift optional. ;)
 
Re: distance for SECs inside the building line

Wow, what great replies all up, thanks so much.
Further digging today, found the thing.

No, it's not in the NEC, yes it's in our Washington Administrative Code (which I know a lot better tonight!)

No, it doesn't mention unfused SE conductors but 15ft for service raceway inside the building, which of course for all purposes amounts to the same thing. Interesting other states are envious/alarmed we allow that far inside. I thought WA had a reputation for being somewhat restrictive.

Thanks charlieb for the slab info. Good to know.

Thanks suemarkp, yes I am on the WA L&I listserv, do have the latest WAC, just needed to read it better.

Thanks Tom Baker, is there website/info for your classes in WA?
-Tim

[ November 19, 2005, 02:23 AM: Message edited by: TimWA ]
 
Re: distance for SECs inside the building line

Originally posted by TimWA:Thanks Tom Baker, is there website/info for your classes in WA?
I know there is, and I know how to get in touch with him. However, as we do not permit advertising on the Forum, you will have to send Tom a Private Message (PM) to get that information. But first, you will have to enable PMs by making a change to your profile. There is an FAQ item that talks about PMs.
 