I looked at a job today and the existing residential meter base is sitting diretcly above the gas meter. Isnt it required to be 5' from the gas meter?
As far as I know, the NEC has no requirement OTHER THAN, not "directly over". 110.26 would make that a violation: (3) Height of Working Space. The work space shall be clear and extend from the grade, floor, or platform
I looked at a job today and the existing residential meter base is sitting diretcly above the gas meter. Isnt it required to be 5' from the gas meter?
Gus, does that refer to meters which are generally the poco's.