Re: Distance from Remote Meter to Service Panel?
Originally posted by hurk27:
Even though this house might not ever see the 200 amp service fully loaded, any large motor as in a AC unit will produce a large startup load that will dim lights if the service is even half loaded. :
Originally posted by james wuebker:
This is one of the things that I don't agree on is figuring your load for the service. iwire said us 3/0 which is good for 150 amps. Well if I'm putting in a 200 amp service then I think it is good the figure that the load might make it there at some point of time.
These are the types of reasons IMO the code leaves it as a design decision.
There certainly can be times where I agree with James that the VD should be calculated on the full rating but I would not say it needs to be done that way every time.
First think of how we arrived at a 200 amp service, someone did the NEC calculations and came up with a figure that IMO will already be on the high side of reality. The power companies wire sizing tends to support my thoughts here.
This figure may have shown a 160 amp service was sufficient but the next standard size service is typically 200 so now we have a service that is even larger than required.
IMO a 200 amp service to a
typical 1,700 sq ft house is never going to approach 200 amps of load and while we could size the conductors on that IMO the person paying the bill should get some input here if they want to pay for substantially larger conductors for a load that may never happen.
On the other hand if I was told that the people run a machine shop out of the garage I would be thinking the 200 amps may well be used.
My point here is each situation is different and I do not think we would be doing the customers any favors by always figuring worst case.
Get all the facts you can and make an educated design decision.
JMO, Bob