800.52 Installation of Communications Wires and Cables
(A) Separation from Other Conductors
(2) Other Applications
Communication wires and cables shall be separated at least 50mm (2in) from conductors of any electric light, power, Class 1, non-power-limited fire alarm, or medium power network-powered broadband communication circuits.
Exception No 1: Where either (1) all of the conductors the electric light, power, Class 1, non-power-limited fire alarm, or medium power network-powered broadband communication circuits are in a raceway or in metal sheathed, metal clad, non-metallic-sheathed, type AC, or type UF cables, or (2) all of the conductors of communications circuits are enclosed in raceway.