- Location
- Bremerton, Washington
- Occupation
- Master Electrician
Macmikeman. I answered this above but here is the code reference:
725.55 (A) Cables of class 2 circuits (doorbell) shall not be placed in the same cable, outlet box, ...., with any conductor of electric light,power or class 1 circuit.
see definition of conductor. A NM cable is a contains conductors and is a chapter 3 wiring method. If you accept that doorbell wire can run alongside rigid conduit or MC cable, then it can run with NM cable in the same stud hole.
725.55 (A) Cables of class 2 circuits (doorbell) shall not be placed in the same cable, outlet box, ...., with any conductor of electric light,power or class 1 circuit.
see definition of conductor. A NM cable is a contains conductors and is a chapter 3 wiring method. If you accept that doorbell wire can run alongside rigid conduit or MC cable, then it can run with NM cable in the same stud hole.