Re: Distance of meter from panelboard
Stopped by today to BS with a roofing contractor. Walking through the house he has been rehabbing I notice the cover was off the breaker panel. I was asked what I thought about his service. Bad habit of looking. AT the Mall, in the gym at school, I'm always looking at the electrical work. You guys know how that is. Anyway....SEC in PVC down to an LB through the mud sill, laying on the ground in the crawl space up the wall into the breaker panel. I said the main's not bolted in. You can pull it off the bus while it's energized. "Why would anybody want to do that? The cover will keep it in !" But the cover's not on now, it's a code violation. Normally the AHJ will allow 10' without a disconnect under the meter. This run is 35-40' I pointed out the pole with the transformer on it and the five service drops. Told him the transformer is probably fused about 800amps to handle those five drops. The SEC would melt and start a fire before it blew the fuse on the transformer. "Well he must have known what he's doing, that's what he does for a living." OK Then, typical day, small town America. I also like that signature. Just don't be fairly safe !
Hell with it! I think I'll go fishing ! Dan