Distance requried between telecommunication cables& Power cables
elecman72
hi to all
Pls , i would like to know the required distance between telecommunication cables & power cables according to NEC , ANSI
Regards
thx
thx
Thx e57
i have this article ,, but it doesnt give me the required distance from transformers , motors .........................................................................( Similarly, telecommunications cabling is routed
away from large motors, generators, induction heaters, arc welders, x-ray
equipment and radio frequency, microwave or radar sources )
it just mentioned away , if 1 m is enough or need more
thx
1 meter is roughly 3 feet right? :grin: Anyway it would depend on the voltage and EMF/RF noise of the circuit. Of course those type things like transformers and motors with cause more EMF - and more so at higher voltages - but not really spelled out in many places. In either the NEC or ANSI - the further the better would be best beyond 5" for 2000 watts, and 2' at 5kVA. The 02 NEC says only 2" in 800.52(A)2... I call that a judgement call....
iwire said:
How close to motors and transformer would you run communication circuits without them being in metal raceways?
Slightly closer - but since no distance is really given - still a judgement call - but avoidance is best.... Nothing like a hummy phone line....
Communication cables will be in metal racway sure , but there is a distance required to be away from transformers or motors ,
Try these articles,
Also their may be help full answers to your other thread about grounding of telecomunications and IT
08 NEC ART's 725 - 760 - 770 - 800 - 820 - 830