I agree the gennie's and transformer primary's neutrals should be tied together directly, i.e not through the HRG xfmr. Additionally, this connection should should not be solidly grounded at any point. The xfmr frame should be tied to the ground grid.I apologize for the confusion. In the one line I posted, yes, I did depict a wye/delta transformer. That is one of our more typical plants, not the one in question. I attached it because I am in disbelief that the generator neutral should be directly tied to the transformer neutral as Besoeker states (bypassing the HRG setup). It is not a representation of the plant that we were originally having the problem with. I have attached a one line of the plant in question.
I believe you mean your utility is 3?, 3-wire only... i.e. essentially delta.Our utility does not (?) provides us with a delta connection (i.e. no neutral). Why a wye/wye transformer was chosen is beyond me. To be frank, 20 years ago when the plant was built, the company probably got a smoking deal on the transformer and decided to use it.
Strictly speaking, 3? line-to-line voltages can be wye-supplied without the neutral or delta supplied, with no difference in transmission or usage (as long as they are in sync :grin